Wire size... ?

What size wire do you use when installing DC lights?
Thanks...
Squeaks is offline  
Sponsored Links
Advertisement
 
post #2 of 10 (permalink) Old 08-30-2012, 07:10 PM
Frequent Contributor
 
Join Date: Dec 2010
Location: pa
Posts: 701
Back To Top
Re: Wire size... ?

What kind of lights? What is the distance, you have a bigger voltage drop in dc then you do in ac .
jakesroost is offline  
post #3 of 10 (permalink) Old 08-31-2012, 07:42 PM
Frequent Contributor
 
boyswillhunt's Avatar
 
Join Date: Apr 2002
Location: Gilbertsville Pa Montgomery co.
Posts: 772
Back To Top
Re: Wire size... ?

Divide your wattage by your voltage, = amperage, and use the wire size larger then that.
14 for 15amp
12 for 20 amp
10 for you have too many lights there...

"Here are the roughs and beards and space and ruggedness and nonchalance that the soul loves"
boyswillhunt is offline  
Sponsored Links
Advertisement
 
post #4 of 10 (permalink) Old 09-03-2012, 02:49 PM Thread Starter
Diehard Outdoorsman
 
Squeaks's Avatar
 
Join Date: Feb 2006
Location: Bellefonte, Pa
Posts: 3,823
Back To Top
Re: Wire size... ?

Each run from the fuse box panel will probably be 30' tops. I have to see what the watts are on the lights. They came with the camp and haven't been installed yet.
Thanks for the help...
Squeaks is offline  
post #5 of 10 (permalink) Old 09-10-2012, 05:19 PM Thread Starter
Diehard Outdoorsman
 
Squeaks's Avatar
 
Join Date: Feb 2006
Location: Bellefonte, Pa
Posts: 3,823
Back To Top
Re: Wire size... ?

The lights are 12 watts.
Squeaks is offline  
post #6 of 10 (permalink) Old 09-10-2012, 05:37 PM
Frequent Contributor
 
Join Date: Dec 2010
Location: pa
Posts: 701
Back To Top
Re: Wire size... ?

rough calculations in my head is 8 of those lights would equal 1 amp and using the 80% rule using 14 awg wire on a 15 amp breaker you could have up to 12 amps on that circuit or 96 of those lights and 30' not enough to worry about.
jakesroost is offline  
post #7 of 10 (permalink) Old 09-10-2012, 07:06 PM
The Man
 
Buk_Huntir's Avatar
 
Join Date: Nov 2005
Location: PA, 5C, 3D, 2E
Posts: 5,582
Back To Top
Re: Wire size... ?

Why are you running DC? Is this all off battery power?

I'm very important. I have many leather-bound books and my apartment smells of rich mahogany.
Buk_Huntir is offline  
post #8 of 10 (permalink) Old 09-10-2012, 09:39 PM Thread Starter
Diehard Outdoorsman
 
Squeaks's Avatar
 
Join Date: Feb 2006
Location: Bellefonte, Pa
Posts: 3,823
Back To Top
Re: Wire size... ?

Yes... this will run off a battery with a fuse panel.
Thanks for the help...
Squeaks is offline  
post #9 of 10 (permalink) Old 09-11-2012, 04:33 AM
Regular Visitor
 
Join Date: Apr 2010
Location: WMU 2F
Posts: 73
Back To Top
Re: Wire size... ?

You might want to rethink that, with size 14 wire I wouldn't go over 3 lights (that's 36 watts or 3amps). With 4 12watt lights you would be drawing 4amps and with #14 wire the recommended maximum safe circuit length is only 18ft. Once you start to get into the 15 to 20 amp range you will need #10 or even #8 size wire. That's the big problem with 12v systems running circuits of any length. My suggestion is to use a DC to AC inverter to switch to a standard 120v system and then you can use #14 wire safely. The other benefit is you can run standard lights and appliances and easily switch to a generator if or when the batteries die.

Dad, I think I got a 10 point!

RidgwayCamper is offline  
post #10 of 10 (permalink) Old 09-11-2012, 05:15 PM
Senior Member
 
Join Date: Oct 2001
Location: lancaster
Posts: 12,033
Back To Top
Re: Wire size... ?

Each way has it's advantages and disadvantages.

A friend built a house which remained off the grid for the first five years. He wired the house normally as if for 120 volts, but put 12 volt light bulbs in the fixtures and a bank of batteries in the basement which were connected to a small wind mill and a solar panel. flip the light switch in the wall and the light went on in the ceiling. When he switched to grid power all he had to do was connect the main box to the power company and change to 120 light bulbs. Unless you want separate dual voltage systems, wiring for 120 once makes sense. If the 12 volt is permenent then you want different wire, so folks coming along later can identify the difference and won't tie them into each other.

He also had several 12 volt appliances, coffee maker, electric saucepan, tv etc. he made up a 110 plug to 12 volt socket extension cord to run the appliances until he went with the grid power.
zimmerstutzen is offline  
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the The HuntingPA.com Outdoor Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.

User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in










Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome