Camp crawl spaces- question on sealing?

I've been doing a lot of researching on buildings with crawl spaces. I see that a lot of homes with crawl spaces are closing off traditional block wall vents, adding vapor barriers to the walls, over the dirt floors, even insulating between the floor joists at the sill plate. Any thoughts on this as it relates to camps, that are only seasonally heated and used?

Wishing I was at camp!
Hittingguru is offline  
Sponsored Links
Advertisement
 
post #2 of 4 (permalink) Old 03-08-2015, 08:36 PM
Regular Member
 
blueridgehunter's Avatar
 
Join Date: Dec 2012
Location: westmoreland /camp forest county
Posts: 1,514
Back To Top
Re: Camp crawl spaces- question on sealing?

We put plastic on the ground topped with gravel then insulated the floor joists and covered that with osb. Was a pain but helps keep the floor from feeling like a popsicle.

live laugh love and hunt hard!

Forest county got to love it!
blueridgehunter is offline  
post #3 of 4 (permalink) Old 03-08-2015, 09:01 PM
Regular Member
 
Join Date: Aug 2002
Posts: 1,526
Back To Top
Re: Camp crawl spaces- question on sealing?

6 mil vapor barrier for floor covered with limestone, insulate joist space with unfaced R-30 to R-38 fiberglass batt insulation and cover all of that with fsk vapor barrier. Keep vents in wall sufficient in size to meet code and install in one or two of them a muffin fan to turn the air in the crawlspace over quickly.
Doubledog is offline  
Sponsored Links
Advertisement
 
post #4 of 4 (permalink) Old 03-09-2015, 09:05 PM
Diehard Outdoorsman
 
WexfordBowhunter's Avatar
 
Join Date: Jan 2010
Location: Wexford, Pennsylvania 15090
Posts: 3,706
Back To Top
Re: Camp crawl spaces- question on sealing?

First of all, I hate crawl spaces. I do a lot of insurance investigations of rotted framing over insufficiently vented crawl spaces. The code requires one square foot of net free venting area (NFVA) for every 150 square foot of crawl space. Vents should be located to provide cross flow and one vent within 3 feet of each corner. A typical 8 x 16 louvered block vent provides about 64 square inches of NFVA each. The venting requirement can be reduced to 1 square foot for every 1500 square foot of crawl space if you use a vapor retarder with sealed seams and sealing of the barrier to the stem walls. You also need a drainage system to prevent the accumulation of water. I also recommend insulation around the perimeter to prevent warmer air from condensing on the cold exterior walls. As mentioned above, mechanical venting is an option, but if used, should run continuously. Did I already mention that I hate crawl spaces?
WexfordBowhunter is offline  
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the The HuntingPA.com Outdoor Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.

User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in










Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome