Frozen Radon Mitigation System

I recently had a radon system installed in my newly purchased house. The exhaust pipe exits the rear of the house above grade as it is a walk out basement. Upon exit there is a 90 degree elbow and the pipe runs horizontally along the outside of the house for about 15'. At this point there is another 90 degree elbow, then the ventilation fan then the pipe continues straight up above the roofline.

The system has frozen up twice in the last month with this cold weather. It's seems the horizontal pipe on the outside is full of water. I was curious if it is normal for radon systems to freeze? I would suspect the warm air from inside the house would cause condensation in the pipe, but is it enough to fill a 3-4" pipe with water?
greenstang232 is offline  
Sponsored Links
Advertisement
 
post #2 of 11 (permalink) Old 01-27-2014, 02:02 PM
Part of the Community
 
Join Date: Nov 2008
Location: Erie, PA.
Posts: 210
Back To Top
Re: Frozen Radon Mitigation System

I too have a mitigation system and water will collect in the pipe from condensation. Normally when the install the pipe into the basement floor the pipe has weep holes to allow the water to drain out. Mine does not have weep holes and when the water collects you can hear it slushing
around. I have not fixed it since I have radiant in floor heat in my basement and did not want to break one of the lines.
Mine seems to collect on the inside, sounds like you have one too many 90's...
BuckSlayer1B is offline  
post #3 of 11 (permalink) Old 01-27-2014, 03:02 PM
Diehard Outdoorsman
 
Join Date: Aug 2004
Location: Washington PA
Posts: 4,887
Back To Top
Re: Frozen Radon Mitigation System

Can you put a T in the line to let it drain?

The United States of America has the greatest people on earth.
Deer archer is offline  
Sponsored Links
Advertisement
 
post #4 of 11 (permalink) Old 01-27-2014, 04:09 PM Thread Starter
Regular Member
 
greenstang232's Avatar
 
Join Date: Jun 2006
Location: Harrisburg, Pa
Posts: 2,422
Send a message via AIM to greenstang232
Back To Top
Re: Frozen Radon Mitigation System

I thought about putting a T into the pipe and running it into a corrugated drain pipe but I didn't know if that would affect the system running properly.
greenstang232 is offline  
post #5 of 11 (permalink) Old 01-28-2014, 01:06 AM
Diehard Outdoorsman
 
Join Date: Aug 2004
Location: Washington PA
Posts: 4,887
Back To Top
Re: Frozen Radon Mitigation System

http://www.radongas.com/troubleshooting.htm
I realize links to exterior are frowned upon. So sorry but I could never type all the info.
Greenstang, the attached link suggests to do nothing when the pipes freeze.

The United States of America has the greatest people on earth.
Deer archer is offline  
post #6 of 11 (permalink) Old 01-28-2014, 10:42 AM Thread Starter
Regular Member
 
greenstang232's Avatar
 
Join Date: Jun 2006
Location: Harrisburg, Pa
Posts: 2,422
Send a message via AIM to greenstang232
Back To Top
Re: Frozen Radon Mitigation System

Thanks for the link archer
greenstang232 is offline  
post #7 of 11 (permalink) Old 01-28-2014, 12:54 PM
RIZ
Diehard Outdoorsman
 
Join Date: Apr 2000
Location: butler county, pa
Posts: 2,803
Back To Top
Re: Frozen Radon Mitigation System

putting in weep hole or "T" would comprimize the system. the vacuum is pulled from under the floor slab and not the room air.

RIZ
RIZ is offline  
post #8 of 11 (permalink) Old 01-28-2014, 01:07 PM
New Arrival
 
Join Date: Dec 2009
Location: Lebanon pa - Tioga Pa
Posts: 11
Back To Top
Re: Frozen Radon Mitigation System

Greenstang,First off I am a certified Radon Mitigator in Pa. I would first ask why there is a 15' run off horizontal pipe, second is there a "Drain to ground" fitting just above the fan where it would allow the water to pass though the fan and back to ground! Third, and most impotantly, did a CERTIFIED RADON MITIGATOR install the system! Too many times a friend or a plumber says they "know" how to install, but the truth is they dont know how and is very illegal for them to do it, unless they are "CERTIFIED" through the state of Pa D.E.P. Puttingt an inline tee before the fan will result in system not pulling the radon out of your home!!! Systems are designed to pull moisture from below the concrete, thus the ice and water build up. However being a certified mitigator, there is a formula for the fan sizing to be properly fitted for your home, which if not done properly could lead to other serios problems, not just water in the pipe! First one would be back drafting of flue gases from your heat source!
SkiRev is offline  
post #9 of 11 (permalink) Old 01-28-2014, 05:55 PM Thread Starter
Regular Member
 
greenstang232's Avatar
 
Join Date: Jun 2006
Location: Harrisburg, Pa
Posts: 2,422
Send a message via AIM to greenstang232
Back To Top
Re: Frozen Radon Mitigation System

Skirev,

The easy explanation as to why there is 15' of horizontal pipe is the basement is finished and where the pipe exits there would have had to be five 90 degree elbows if the pipe were to go straight up upon exit bc of floor and soffit overhangs. I do not believe there is a drain after the fan. Yes it was installed by a certified radon mitigator. I will send yiu a pm tonigh after I check if there is a drain. Thanks!
greenstang232 is offline  
post #10 of 11 (permalink) Old 02-10-2014, 10:26 PM
New Arrival
 
Join Date: Nov 2013
Location: pa,bradford county
Posts: 34
Back To Top
Re: Frozen Radon Mitigation System

Skirev,

What are they charging for a radon system these days?
hankf is offline  
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the The HuntingPA.com Outdoor Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.

User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in










Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Posting Rules  
You may not post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome